Originally Posted by
Bunbury
You can pretty much ignore the change in density unless you're thinking of very large temperature changes. The heat picked up by the water is m.Cp.Dt where m is the mass flow rate, cp the specific heat and Dt the rise in temperature (all in consistent units of course). For PC surely you'll only need 6mm tubing for the sort of flowrate you'll be using.
For a start what's the total heat you need to remove, in Watts?
Hang on, when you mention change in density, are you envisaging a thermosyphon, i.e. no pump required?