    Any one of you that know UPS designing with all respects, please follow from the simple example and design from start to end. Please share your knowledge for all of Us. I personally need to know this.


    Reply With Quote  
     

  2.  
     

  3. #2  
    Cooking Something Good MacGyver1968's Avatar
    Join Date
    Aug 2006
    Location
    Dallas, Texas
    Posts
    2,051
    Here ya go:



    Fixin' shit that ain't broke.
    Reply With Quote  
     

  4. #3  
    New Member
    Join Date
    Jan 2013
    Posts
    2
    This is circuit diagram. I need load designing. Like if there are 50 servers taking power of 220V* 10A* 50 = 110,000Watts = 110KW So for 110KW what would be the size of UPS if i need a) 15mint full load back up b) 1hour half load backup c) 1hour full load backup etc.
    Reply With Quote  
     

  5. #4  
    Cooking Something Good MacGyver1968's Avatar
    Join Date
    Aug 2006
    Location
    Dallas, Texas
    Posts
    2,051
    Fixin' shit that ain't broke.
    Reply With Quote  
     

  6. #5  
    Forum Freshman
    Join Date
    Oct 2012
    Location
    Provence (South east of France)
    Posts
    93
    First, you have to compute the energy that must be available from you system. Energy is expressed in Joules (J) and is equal to power multiply by duration in seconds.
    In you example, the power is 110KW. Let suppose you want a duration of 15mn, that is 900s. The energy you need is 110KW x 900 = 99000 KJ.

    The capacity of an accumulator is generally expressed in A.h.
    One A.H is 1 A during 1 hour or 2 A during 0.5 hour ...
    The energy that can be stored in an accumulator, V x A x duration = V x Capacity x 3600.
    For instance, a typical car accumulator has characteristics such as 12V 70 A.h. The energy that can be stored in such a device is 12 x 70 x 3600 = 3024 KJ.

    So, knowing the required energy, you may compute the number and characteristics of the accumulator system.
    Ammar_Soliman likes this.
    Reply With Quote  
     

Similar Threads

  1. Designing Primers
    By Deoxy74 in forum Biology
    Replies: 8
    Last Post: September 26th, 2011, 12:14 PM
  2. Need help with 35W CO2 laser power supply.
    By laserlover in forum Electrical and Electronics
    Replies: 2
    Last Post: August 19th, 2011, 11:04 AM
  3. Voice crack in grown ups
    By Raziell in forum Biology
    Replies: 2
    Last Post: June 26th, 2011, 06:44 AM
  4. Telephone and power supply
    By mohana in forum Electrical and Electronics
    Replies: 1
    Last Post: May 25th, 2009, 10:19 AM
  5. Computer crashes (Power supply?)
    By (In)Sanity in forum Computer Science
    Replies: 2
    Last Post: January 16th, 2005, 11:58 PM
Bookmarks
Bookmarks
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •